Joseph: Please see V. C. Summer’s
responses below.
Bill Bell
Reactor Engineering
V. C. Summer Station
803-345-4389
From:
pwrrm-bounces@retaqs.com [mailto:pwrrm-bounces@retaqs.com] On Behalf Of WILLETT, JOSEPH E
Sent: Tuesday, February 06, 2007
3:05 PM
To: respvr@retaqs.com;
Subject: [Pwrrm] Secondary
Calorimetric Feedback Needed (PWR) – Heat Balance(BWR)
To All,
I apologize, this is a repeat Request, but the HIT
Team I’m working on needs more specific information regarding secondary
calorimetric calculations. I could use a reply by February 15th.
We have not implemented Appendix K using ultrasonic
flow measurement for Main feedwater as of yet.
Our Question(s)
1) What are other plants goals/expectations for
maintaining power level? (=/- MW or goal);
-How easy is it to maintain?
-Is there a band within which you operate? What is it?
Is it maintained?
There is no specific band established. The attached OAP-100.06
specifies the maximum allowable power levels and durations.
-What procedure or guidance is provided to your
operators?
OAP-100.06, Section 10
-Can I get a copy of the procedure?
Yes, it is attached to this email.
2) How is your secondary calculation performed?
(Averaging Inputs, Instantaneous values, combination)
-Is it a module or program on your plant computer or
is it an off-line routine?
We use a computer program running constantly on the plant computer.
-What is the frequency of the calculations utilized? (1 sec, 1 minute, 10 minutes 30 minutes, etc…)?
The plant computer executes the program once a second.
-What is the frequency of the scan rate for input
parameters utilized? (1 sec, 1 minute, 10 minutes 30 minutes, etc…)? Does
it vary by parameter? Are they averaged, and for how long? (30 seconds, 60
seconds, etc...)
The scan rate for all of the calorimetric inputs (pressures, flows,
temperatures) is once a second.
-What is there BASIS for the calculation? Is
there supporting documentation? What is it?
The FSAR specifies that a feedwater flow rate based calculation will
be used for complying with the plant license.
-What frequency do the operators control to? (2 minute
average, 10 minute average, 30 minute average, etc….)
As discussed in the attached OAP-100.06 the operators control to an
8 hour average power level.
3) Are your temperature and flow transmitters set
specifically for this calculation? (dampening or bias settings)
All of the instruments that feed the calorimetric calculation are
calibrated every 18 months and op tested once a quarter. They do not
employ any special dampening.
4) Are any of your control loops (Feedwater) used in
the secondary calorimetric calculation?
Yes, Feedwater flow rate and steam pressure instrumentation
also provide protection and control functions.
5) Have you had any issues related to power swings or
related to your secondary calorimetric?
Yes, a continuing problem we have here are feed flow spikes in our A
loop. We have been investigating the cause of this problem but have not
yet found the cause.
6) Who has ownership/control of your program/logic?
System Engineering, Design Engineering, Operations, Reactor Engineering or some
other department?
Reactor Engineering owns the calorimetric program.
----------------------------------------------------
Joseph E. Willett, P.E.
Principal Reactor Engineer-Fuel
Nuclear Operations Division
E-mail: jwillett@oppd.com
Omaha Public Power District
Phone: (402) 533-7213
Ft. Calhoun, NE 68023-0390 FAX: (402) 533-6747
Mail Station: FC-1-1 Plant
----------------------------------------------------
--------
|