At VC Summer, we use Gammametrics intermediate range instruments
to feed our reactivity calculation on the plant computer during LPPT (using boron
dilution). So we don’t have any experience with DRWM or power range
NIs.
1 – no
2 – n/a
3 – n/a
4 – We do a doubling time test that has to match within 4%
of the predicted reactivity for a given startup rate. Also, the detector
has to pass the statistical reliability (chi squared) test.
5 - no
From: pwrrm@retaqs.com
[mailto:pwrrm@retaqs.com] On Behalf Of Gore, Duane
Sent: Monday, May 03, 2010 10:50 AM
To: 'PWR Reactivity Management'
Subject: [Pwrrm] Use of Power Range NI Detectors for Low Power Physics
Testing
At STP we use one of our power range nuclear instrumentation (NI)
detectors for our reactivity measurements during low power physics testing
(LPPT). Recently, on the Unit 2 cycle 15 startup, the gamma compensation
(bucking) current for the lower half of the NI detector used for the
measurement behaved in an atypical manner. Although the reactivity computer
passed its checkout test, the measured worth of the heaviest control rod bank
was over-predicted using Westinghouse’s Dynamic Rod Worth Measurement
(DRWM) technique.
Ultimately, we shutdown the reactor, checked connections and
cables, and switched NI detectors. The reactor was restarted and LPPT was
successfully performed. Since the NI detectors are used in such a low current
range for LPPT, it was decided that the detector which was unsuitable for LPPT
use would still provide proper response at power.
Once previously we replaced all of the NI detectors after
connecting the reactivity computer and examining detector responses. The
detector cables were inspected found to be degraded. In that case, we had not
begun reactor startup.