Andy,
At Beaver Valley we always reset the
top and bottom of core setpoints for the Movable Incore System following
a detector replacement, or other maintenance that may impact these setpoints.
A few years ago we had a detector that "stuck" in the core during
a flux map. The technicians manually freed the detector which resulted
in the encoder readout being off by several inches. We used our procedure
to remeasure/calculate the top and bottom setpoints.
The process for the setpoint determination
uses the fuel assembly grid locations relative to the active fuel assembly
height from the vendors drawings. When can identify the grid locations
and then calculate the top of the active fuel.
Anthony (A.R.) Burger
Supervisor, Reactor Engineering
FENOC - Beaver Valley Power Station
Phone: (724) 682-4108
Cell: (724) 601-3224
FAX: (724) 682-4250
Email: aburger@firstenergycorp.com
From:
"Kelliher, Andrew
P" <Andrew.Kelliher@cengllc.com>
To:
"pwrrm@retaqs.com"
<pwrrm@retaqs.com>
Cc:
"Dautel, Robert
G" <Robert.Dautel@cengllc.com>, "Connor,
Kenneth J" <Kenneth.Connor@cengllc.com>,
"Lazzaro, Joseph" <Joseph.Lazzaro@cengllc.com>
Date:
01/18/2013 10:01 AM
Subject:
Re: [Pwrrm]
Moveable Incore Top of Core Values Following Detector Replacement
Sent by:
pwrrm@retaqs.com
Has anyone had to change their top of core
values,
after resetting the withdrawn limit switch to 0”, on the moveable incore
system by several inches following a detector replacement when no physical
dimensions have changed (i.e. just a one for one detector replacement)?
If yes, what was the cause of this change?
Any feedback (i.e. yes or no) would be
valuable. I’ve included some background at the bottom of this e-mail.
Thank you in advance for your help.
Thanks,
Andy
Andrew Kelliher
Reactor Engineer
R.E. Ginna Nuclear Power Plant
Phone: (585) 771-3457
"I'm just sayin', I
don't like fun." - Karl Pilkington
During Ginna’s 2012 Fall Outage the flux
mapping system was replaced. This included replacement of the equipment
in containment (drive boxes, transfers, etc) and in the control room. During
the 75% flux map one of the new detectors failed and was replaced last
month.
On the old system replacement included
manually lining up the detector in containment with the WLS and rezeroing
the encoder. Following this rezeroing, passes were able to be taken using
the previous top of core and bottom of core values without issue.
On the new system this is performed by
driving the detector forward from the control room and then telling the
system to drive to zero position which looks for the WLS and rezeroes the
resolver. However, after this detector replacement all of the top of core
values were altered by several inches.
>>> This e-mail and any attachments are confidential,
may contain legal,
professional or other privileged information, and are intended solely for
the
addressee. If you are not the intended recipient, do not use the
information
in this e-mail in any way, delete this e-mail and notify the sender. -IP2_______________________________________________
PWRRM mailing list
PWRRM@retaqs.com
http://www.keffective.com/mailman/listinfo/pwrrm
-----------------------------------------
The information contained in this message is intended only for the
personal and confidential use of the recipient(s) named above. If
the reader of this message is not the intended recipient or an
agent responsible for delivering it to the intended recipient, you
are hereby notified that you have received this document in error
and that any review, dissemination, distribution, or copying of
this message is strictly prohibited. If you have received this
communication in error, please notify us immediately, and delete
the original message.