From: Hawes, Mark W [mailto:mwhawes@duke-energy.com]
Sent: Wednesday, January 16, 2008 10:22 AM
To: pwrrm-bounces(a)retaqs.com
Subject: FW: [Pwrrm] Point Beach Question:
At Catawba (Westinghouse-4 loop) we don't have issues with DRPI (rod
position indication) associated with rx vessel head ventilation. We do,
however, withdraw each control rod beyond "end of travel" . . . hard stop
position is 231 Steps Wd at CNS, so rods are withdrawn to indicated position
of 235. The rods are then reinserted to specified fully withdrawn (parked)
positions.
This evolution is performed upon reaching full power following any unit
shutdown which required reactor trip breakers to be opened. The
acknowledged problem being 1 to 2 steps of uncertainty with regard to where
drive rods are engaged, and withdrawn from, when breakers are reclosed.
Mark Hawes
CNS Reactor Engineering
(803) 831-3855
_____
From: Keller, Lee A
Sent: Tuesday, January 15, 2008 1:47 PM
To: Hawes, Mark W
Subject: FW: [Pwrrm] Point Beach Question:
Pls address
_____
From: pwrrm-bounces(a)retaqs.com [mailto:pwrrm-bounces@retaqs.com] On Behalf
Of VANCE, KEVIN
Sent: Monday, January 14, 2008 4:29 PM
To: pwrrm(a)retaqs.com
Subject: [Pwrrm] Point Beach Question:
Do you step control rods to the end-of-travel to verify rod position for a
Rod Position Indication outside of limits? If not, what method is used to
verify rod position prior to adjusting indication?
Background:
Point Beach has two control rods that exhibit unusual rod position
indication variations. We have shown rod position indication takes step
change swings (+/- 20 steps) following control rod shroud fan temperature
changes. We have moved the control rod drive shaft of these two rods from
bank D control banks to shutdown banks, and the problem has followed the
drive shaft. Most other rod position indications vary by +/- 5 steps, with
no large "swings." Research into why these two drive shafts exhibit
different properties has not been successful. It is believed that these
drive shafts have some residual magnetism causing the Rod Position Detectors
to indicate erroneously. These jack shafts were replaced in 1998.